The charging system (alternator) on the generator engine is used to recharge the battery after a start and will provide much more charging current than the external charger. The external chargers are only meant to keep ahead of the self-discharge rate of the battery.
But this shouldn't matter for an emergency generator intended for home use, where it will only see an occasional start. The trickle charger could have a bulk mode added to it. Just doesn't make sense to add another winding that puts out a few amps that are then sent through a voltage regulator just for the battery, when you already have windings putting out 50+ amps going through their own voltage regulator which the already-necessary trickle charger can use.
Actually, there was no external sign that anything was wrong. I only saw the damage after removing the front panel of the unit. I'm going back today to install the replacement battery, and will explain everything I've learned so far, and look for the charger to disable it.So did you figure out why the generator won't start? :grin:
But really, you think she would have noticed something like that and said something. Maybe like: "You might want to bring out a new battery when you come."
She didn't know, but I wouldn't have slapped a replacement in without the call to Generac (no help so far) and posting about it here, with the brain pool.You sometimes have to take a step back and consider not everyone has this level of intelligence on the issue.
It does, or at least did, start once a week for about 12 minutes.But this shouldn't matter for an emergency generator intended for home use, where it will only see an occasional start.
Actually, there was no external sign that anything was wrong. I only saw the damage after removing the front panel of the unit. I'm going back today to install the replacement battery, and will explain everything I've learned so far, and look for the charger to disable it.
What I'd really like to know is whether there's any recourse to pursue with Generac, now that this problem is a few years old with them. In other words, what are their responsibilities? Have they accepted the problem, and is there any warranty or compensation available?
I installed my 04456 in September 2004. I now have to install my 4th battery due to the "exploding battery syndrome". I'm astonished to read that there are so many others in Florida who have had the same problem. My guess is that the warm, humid, Florida environment exacerbates the trickle charger's "cooking" of the battery. When battery #3 was installed, I had the unit checked by an "Elite" Generac dealer, and I was told that the charging system checked out OK. I specifically asked if Generac had issued a service bulletin regarding this issue. I was told no. On December 3rd, 2007 I discovered battery #3 exploded. I called Generac HQ and was told that there are no known issues with exploding batteries. The very sweet Customer Service Rep at Generac refered me to Kelly Myers and this blog. Certainly there must be a way individualy or collectively that Generac can be coerced to deal with this damaging and dangerous situation.
Actually, there was no external sign that anything was wrong. I only saw the damage after removing the front panel of the unit. I'm going back today to install the replacement battery, and will explain everything I've learned so far, and look for the charger to disable it.
I left it alone. The no-load voltage was 14.1v, and it dropped to around 13.7 with the engine running on manual. I will go back and check the electrolyte level in about 3 months.Temporary is OK, but permanant is not advisable, ...
IMO, that voltage is too high for a "dumb" trickle charger... but I don't know the charging specifics for the battery you are using (and couldn't find any online).I left it alone. The no-load voltage was 14.1v, and it dropped to around 13.7 with the engine running on manual. I will go back and check the electrolyte level in about 3 months.
Thanx for all the info and advice, gang!![]()
IMO, that voltage is too high for a "dumb" trickle charger... but I don't know the charging specifics for the battery you are using (and couldn't find any online).
As a reference, compare to charging information published for Optima batteries: http://www.optimabatteries.com/product_support/charging.php