I'm still having trouble with the "double derating" In the NEC 2008 Handbook at 210.20a it gives as example of a 25A continuous load with 4 Current Carrying Conductors (CCC). It says the calculated load is 25A and to use this with the derating from 310.15b2a this being 25A/.80 = 31.25 to size the conductor to avoid double derating. But I would normally use 25A X 1.25 = 31.25A for a continuous load to size the conductor which would bring me to the same value without derating for more than 3 CCC. The engineer that I'm working with said it makes no sense to him either in that when you have 4-6 CCC there is no affect on the calculations as there would be with just multiplying by 1.25 for a continuous load. How would you interpret this?
Also, at the end of the example it says "where the ambient temperature exceeds 86C" I believe this should be 86F.