Need to add an electric range line and microwave line to a town home, it only has a 100 amp service so I wanted to check the load.
926 sqft * 3 = 2778 VA
small app. 3000 VA
Laundry 1500 VA
General Lighting demand 4497 VA
Range 10.7 Kw @ 8 kw demand from col. C
Furnace 1800 VA
Dishwasher 1800 VA
Microwave 1800 VA
I figured high for the above 3, didn't look at the home and couldn't find exact figures
A/C 3000 VA
Total 20,897/240 = 87 amps