JayHawkInspector
New member
I always thought Romex or NM cable needed to be protected when ran to or through brick veneer? Or am I wrong. The NEC says in 334.12 (8), It cannot be surrounded by or enclosed by concrete mix of any type, also look at 334.12 (10)(b)&(c) and it will elaborate more. So why do electricians think it doesn't need to be protected?