We install automatic gate operators which use 120v motors and 24vac control circuits. When we need to use 2 operators in a master/slave combination to span a large width driveway, the manufacturer supplies the operator with a 40ft cable consisting of 7 14AWG stranded conductors. 3 of those conductors are motor for the motor (120v cond to open, 120v cond. to close, and a neutral) the other 4 conductors are 24vac motor limit wires. We have been told by an inspector that we have to run two separate conduits and separate the 120v from the 24vac. Is this accurate?
I know that if they were separate conductors, we would have to separate them, but if they are in a pre-made cable we would not.