I need some second and third opinions on this please.
Went on an after hours service call the other night to a sprawling apartment complex. The building I went to had twenty-four apartments with two 800 amp mains (twelve apts. per main) one of the mains had been tripping and every time they reset it, it would trip again in a few minutes (maint. guy said about two minutes). When I got there they had the door open and the main reset after about thirty minutes of off time. I looked it over and saw no physical problems everything nice and new looking as it was just barely a year old. A quick check with the thermal thermometer showed that L1 was running about 20 deg. F hotter than L2. I tried to do an amp check but with three paralell 500's it was not easy and I am sure not accurate. I left an hour later and the main was still holding and the block temps had decreased as had the ambient (92 deg F to 86 deg F).
I figured there must be a loose connection somewhere on L1 either at the breaker lug or in the meter bank. Anybody got a suggestion as to what else it might be?
Gene
_______________________________
Remember - Speed Kills and its not always you.
Gene