I'm trying to see what would happen with a 480V motor that had its windings connected in Delta when the motor lost a phase. For this I'm going to assume that a phase was lost on the primary side of the motor contactor, and we are taking voltage readings on the secondary side of the contactor.
For this case I would think that when measuring between one of the two good phases and the lost phase we would read 240V. This is because the two windings that are connected between the two good phases and the open phase will now be in series parallel with the winding connected between the two good phases and will have 480V across the series combination. Seeing that each of the impedances of these windings are equal I would think that 240V would drop across each winding and when measuring across each of these windings including the open phase in the measurement you would see 240V.
Would you also see 240V L-G if you read from this open phase to ground?
For this case I would think that when measuring between one of the two good phases and the lost phase we would read 240V. This is because the two windings that are connected between the two good phases and the open phase will now be in series parallel with the winding connected between the two good phases and will have 480V across the series combination. Seeing that each of the impedances of these windings are equal I would think that 240V would drop across each winding and when measuring across each of these windings including the open phase in the measurement you would see 240V.
Would you also see 240V L-G if you read from this open phase to ground?