CO, remember that receptacles are wired daisy-chained. It's a 50/50 chance that the bad connection is in a working receptacle. It's either in the "last" working one or the "first" dead one.
You can also turn on or plug in a light where the power is out, and have someone watching it while you wiggle receptacles, both working ones around the dead area, and the non-working ones.
	
		
			
		
		
	
				
			You can also turn on or plug in a light where the power is out, and have someone watching it while you wiggle receptacles, both working ones around the dead area, and the non-working ones.
I wouldn't recommend that; the intermittent may reconnect while it's jumped.If MB recep is end of line put a jumper beween hot and neuttral and check continuity on other bedrooms.
			