mc to emt: accessible?

Status
Not open for further replies.

iand74

Member
does a change form mc to emt need to be accessible?

for example, going from an mc connector to a threaded coupling into an emt connector.

I was told that it needed to be accessible but can't find any reference to it in the book.

thanks
 

mcclary's electrical

Senior Member
Location
VA
They make a fitting to do that without using the coupling and no, it does not have to be accessible unless you used a box for the transition.
 

iwire

Moderator
Staff member
Location
Massachusetts
does a change form mc to emt need to be accessible?

for example, going from an mc connector to a threaded coupling into an emt connector.

I was told that it needed to be accessible but can't find any reference to it in the book.

thanks

See the last sentence of 300.15(F)
 