Compact fluorescent in clothes closet
Only if it has a completely enclosed lamp. The idea is to not be able to change out the CFL to an incand. lamp. Besides, with #2, the fixture itself has to be a flourescent type.
I agree with iwire. If the compact fluorescent went bad who's to say that a standard incandescent lamp wouldn't be installed.
Very true.
I would add that the NEC section specifies a fluorescent luminaire it makes no mention of a fluorescent lamp.
Look to the UL listing tag to see what kind of 'luminaire' it is. :)
Very true.
Is it not a fluorecent luminaire if it has a flor. lamp in it ? Is that shell limited to use ? We might be at another one of then WHAT IF situations. If it has the right lamp now then why tag it based on what could happen ?
I had issues with this problem with shower lights. They make an open shower trim listed for wet locations with a special coated bulb installed.
I said what's to stop the HO from installing a standard incandescent lamp. My AHJ said they were listed and leagle.
I said what's to stop the HO from installing a standard incandescent lamp. My AHJ said they were listed and legal.
Inspect for whats there now, not what may happen in the future. :)
Inspecting for what might happen in the future would be like a cop handing out speeding tickets to people who own sports cars because they might speed in the future.
You say that like cops aren't supposed to do that. ;)
The can would be listed as an incandescent luminaire. Placing a compact flourescent bulb into a listed incandescent luminaire does not change the listing of the luminaire.
Chris
I agree with the AHJ.
This is no different then if a homeowner chooses to install the wrong wattage incandescent bulb in a luminaire when the original bulb burns out.
Chris
The reason the NEC changed the word "fixture" to "luminaire" is that a lumiaire is the fixture including the bulb. An incandesent fixture with a fluorecent bulb in it, is still and incandesent fixture. So I would not allow it in a closet unless it met all of the requirements.
Put lipstick on a pig............
Very true.
Sometimes it is difficult to separate in our minds what is written and what we read.
As Bob has mentioned, it specifically states luminaire, not lamp type.
A CFL may be permitted in the incandescent type fixture if there is a lense.
But....be careful about installing CFL in a totally enclosed fixture. There may be heat issues and fire issues. Check out the listing of both the luminaire and the lamp to make sure it is a suitable installation.