Dale Hayes

Senior Member
Non-fusible disconnects can obtain a higher SCCR rating when protected with the appropriate fuses. For example: A 1200Amp non-fusible disconnect switch can be rated at 100kA SCCR when used in conjunction with a 1200amp type 'L' fuse. Where does the fuse go? Does the fuse connect to the line tabs on the non-fusible disconnect switch? Is the fuse mounted to separate fuseblocks? Is there any standard procedure for fusing a non-fusible disconnect? Unfortunately, the manufacturers of the fuse and switch show nothing about assembling the combination.

Con"fused" in Missouri.
 
Non-fusible disconnects can obtain a higher SCCR rating when protected with the appropriate fuses. For example: A 1200Amp non-fusible disconnect switch can be rated at 100kA SCCR when used in conjunction with a 1200amp type 'L' fuse. Where does the fuse go? Does the fuse connect to the line tabs on the non-fusible disconnect switch? Is the fuse mounted to separate fuseblocks? Is there any standard procedure for fusing a non-fusible disconnect? Unfortunately, the manufacturers of the fuse and switch show nothing about assembling the combination.

Con"fused" in Missouri.

The fuse would be located ahead of the subject non-fuse disconnect. A good example would be the non-fuse disconnect could not be used as a service disconnect on a service with an AIC >10k, but it could be used as and equipment disconnect down steam from a the proper fuse in a distribution board.
 
The fuses are installed anywhere upstream of the disconnect.
... Like in an MCC, or panelboard, or a fuseblock in an enclosure.

Jm
 
Non-fusible disconnects can obtain a higher SCCR rating when protected with the appropriate fuses. For example: A 1200Amp non-fusible disconnect switch can be rated at 100kA SCCR when used in conjunction with a 1200amp type 'L' fuse. Where does the fuse go? Does the fuse connect to the line tabs on the non-fusible disconnect switch? Is the fuse mounted to separate fuseblocks? Is there any standard procedure for fusing a non-fusible disconnect? Unfortunately, the manufacturers of the fuse and switch show nothing about assembling the combination.

Con"fused" in Missouri.

The fuses would go in a fusible disconnect upstream of the unfused disconnect.
 
Where does the fuse go?
Obviously, you mean physically, not electrically. As suggested above, the best place for the fuses is the origination of the feeder. If it's a tap, you'll have to add an enclosure for the fuses, unless the switch in question has room for them.

Con"fused" in Missouri.
Cute. :)
 