Reading 408.36 rule, I am wondering if one panel feeds another panel by feed-though-lugs mean... will this violate the code since we do not have protection for 2nd panel expecially if 2nd panel stays in different area?
The second panel is protected by the main in the feed through lug panel. The OCPD in the main panel can not be larger than the rating of the second panel
Great PointJust to add.....Unless any of the tap rules can be applied (240.21).![]()
Here's an example of feed through lugs on a 400 amp panel:
Would that conductor routing not be a violation of 300.3(B) & 300.20 ?
The tap rules only apply to conductors. The second panel must be protected at or below its rating. The statement that said; "The OCPD in the main panel can not be larger than the rating of the second panel", is correct.Just to add.....Unless any of the tap rules can be applied (240.21).![]()
OP doesn't mention specifically whether the second panel is MB or MLO, and to this point everyone is assuming it is MLO. As such, your statement is correct. However, the tap rules can be used if the second panel has a MB and all requirements of the applicable tap rule(s) is(are) met.The tap rules only apply to conductors. The second panel must be protected at or below its rating. The statement that said; "The OCPD in the main panel can not be larger than the rating of the second panel", is correct.
The original post says the second panel does not have protection...if it had a main breaker it would have protection, so it appears to me that the second panel is MLO.OP doesn't mention specifically whether the second panel is MB or MLO, and to this point everyone is assuming it is MLO. As such, your statement is correct. However, the tap rules can be used if the second panel has a MB and all requirements of the applicable tap rule(s) is(are) met.