affordable
- Maine
Where in the code could I find a prohibition against having a main panel installed in a walk in cooler in a commercial establishment ?
Would be awfly cold. I would consider it a storage closet. I would assume every inch to be used for storage. I can't imagine clearance would be maintained.
I doubt it's prohibited. On the other hand, I'd have some reservations about installing the panel in the cooler for the following reason; I've seen 20A breakers outdoors, hold 45 amps at 20 below zero.
No violation about it I know of, but... there may be corrosion issues, as breakers heat up under load, they may draw moisture from the cool air and condense in the panel, and yes, any conduits leaving that area would have to be sealed.
Nothing will condense on a warm object surrounded by cold temps.
I assume that your talking about trailer size "walk-in's" well there is no problem with that. From a trailer size to a whole warehouse it doesn't matter. Where the problems starts is when run circuits that go out of that conditioned space, to another space not at the same temperature.
You'll need to read up on sealing, conduit system's around 501 and temperature changes 300.7 and all their requirements. Not all will require seal-off but just keep it in mind if even just going from sub-zero to just stand A/C spaces, as an example!
true but warm air coming in through the conduit, hitting the cold breakers and insides of the panel will.
every conduit that inters or leaves that space would have to be sealed as per 300.7(A) requirement.
I agree and would never say otherwise.
Warm air coming into the panel would kill it quickly, no maybe about it.
You bet.
But we digress, the OP was asking for a "prohibition against having a main panel installed in a walk in cooler" and I don't believe there is one. All other parts of the code would have to be followed just like any panel location.![]()
No seal offs would ever be required for a non hazard location, 300,7(A) only requires a sealing compound on the end or the conduit, like Duct seal or similar, it just has to be approved for the purpose. look at the last sentence in 300.7
You do understand that breakers are regularly installed outdoors in cold climates?
If you are really concerned you can get correction factors to use breakers in high or low temp extremes.
I have seen Hid's in extreme low temp freezers that had Icicles hanging off of them, no penetrations to outside, only penetration was at switch on wall 20' down, sealed on both sides.
Or you would never defog you windshield in your car.:roll:
If walk in is considered a wet/damp location you cannot put panel there. Check with your inspector, he should know.