Using 1 leg of 3p brkr
SiddMartin
PA
Have a spare 3p brkr 480v in existing panel, I want to use 2 poles for 1 ckt (480v) and the other pole for 2nd ckt (277v). Can't think of a code vio, only inconvience if either ckt would trip causing the other ckt to lose pwr as well.
any issues?
This is from the UL White Book, page 12 of the the:
Marking Guide
Molded Case Circuit Breakers
34.
3-Pole ? 1-Phase Rated ?
3?pole circuit breakers are suitable for use on 3-phase systems only, unless marked to indicate use on 1-phase systems, such as, ?For 1?phase connections, use two outside poles,? or an equivalent statement. A 3-pole breaker used in place of a 2-pole breaker on a 3-phase system, such as a 2-pole breaker used in a branch
circuit that is actually two legs of a 3-phase system, is acceptable without the 3-pole breaker being specifically marked."
Sid,
I hope this helps.
A 3-pole breaker used in place of a 2-pole breaker on a 3-phase system, such as a 2-pole breaker used in a branch circuit that is actually two legs of a 3-phase system, is acceptable without the 3-pole breaker being specifically marked."
Seems the second sentence says the opposite of the first sentence; what am I missing?
The first sentence says you can not connect a 3 phase breaker to a single phase source.
The second sentence says you may connect a single phase load to a 3 phase breaker.
You'd never want to do that with a MWBC. That would place both hots on the same phase.
any issues?
Is there even a neutral available for the 277V circuit? Many 480V panels don't supply neutrals
Think legal but really bad idea. It will be a problem later for someone. If they understand and saying yes to save money then be sure to get a letter signed by owner so this does not come back to bite you. Yes safe but might not end up as smart way to go.