Looked at adding another meter to this mess today.

DSC_5418.jpg


DSC_5419.jpg



Fire away!.....

 

RUWired

Senior Member
Location
Pa.
where do the other masts go. I see 3 weather heads and only 2 pipes coming down.
Are those disconnects or meter sockets?
the third one goes down the drain spout for heat tape.

It looks like the others go inside the building. the 3/4 is for the metering
 
Last edited:

masterinbama

Senior Member
It looks to me that the 2 masts on the right go into the building and the meter is CT'd. while the one on the left appears to be tapped ahead of the CT's.

No grouped disconnects for the 2 services, triplex crossing the top of the building more than likely doesn't have the proper clearance.
 
Last edited:

donselectric

Senior Member
Location
nh
a little more info would be nice.. 4 risers 2 cans ?
how is that emt coming out the side of the socket... looks a little funny
what size are the service conductors in the 3/4 emt ??
 

RUWired

Senior Member
Location
Pa.
would 230.29 and 24 apply

230.29 Supports over Buildings.
Service-drop conductors passing over a roof shall be securely supported by substantial structures. Where practicable, such supports shall be independent of the building.

(A) Above Roofs. Conductors shall have a vertical clearance of not less than 2.5 m (8 ft) above the roof surface. The vertical clearance above the roof level shall be maintained for a distance of not less than 900 mm (3 ft) in all directions from the edge of the roof.
 

480sparky

Senior Member
Location
Iowegia
a little more info would be nice.. 4 risers 2 cans ?
how is that emt coming out the side of the socket... looks a little funny
what size are the service conductors in the 3/4 emt ??

Meter on right is on CTs at the WH. Meter on left is self-contained. ? EMT would be 12s from the CT to the meter.
 

PCN

Senior Member
Location
New England
I'll bet you start fresh, new riser, guyed independently, new meter enclosure and don't touch the existing. Tough part is getting around that rain gutter.

As far as violations I don't see a ground wire, and the POCO wire seems to travel over the flat roof for quite a distance without proper clearence. Set a new pole.
 
Last edited:

masterinbama

Senior Member
I'll bet you start fresh, new riser, guyed independently, new meter enclosure and don't touch the existing. Tough part is getting around that rain gutter.

As far as violations I don't see a ground wire, and the POCO wire seem to travel over the flat roof for quite a distance without proper clearence. Set a new pole.

I don't see a ground wire either. But I also don't see what would have been considered the "service" at the time this was installed.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Heat cable
Resistive heat cable used for De-icing, or heating.
used in cold climates to keep gutters/ downspouts from freezing. It's used also for manufacturing plants.
 