Gentlemen,
I have to design an earth mat for a substation whose area is very small, i.e. 20 mtr x 9.5 mtr, soil resistivity is 365.1 Ohm Mtr, Fault Current - 26.2 KA, Duration of Fault Current - 3 Seconds
I tried to design the earth mat system as per IEEE80 but area being very small, the attainable touch & step potential is much more than calculated value, the grid resistance is also coming about 10 Ohms and that make the system totally unsafe.
Can somebody guide me:roll: how to go about designing the system and how to reduce the soil resistivity value to bring it down to, say 30 Ohm Mtr.
regards,