I'm having a tough time finding a replacement 30kva dry transformer to go from 480/277 wye 3 phase to 240/120 delta 3 phase. Most choices are either 480delta 3 phase to 240 delta w/ 120V lighting tap or 480 delta to 240 delta. This is the second transformer to go bad (probably due to lightning). The first one had the usual H1,H2,H3 and X1,X2,X3,X0 connections with X0 going to the neutral bar in the sub panel and ground strap on transformer. The second (present) transformer, which just bit the dust, was a 480 delta to 240 delta configuration with the 120V midtap. The only difference that I could see is that there was an X4 terminal instead of X0. The subpanel neutral was connected to X4 in this case which doesn't seem correct to me. I was under the impression that X4 would be for the 120V midtap.
My question is, can I connect 480/277 wye to a 480 delta transformer and still power a subpanel that has a 240V 3 phase pump motor and (2) 120V circuits w/o any problems????
Any help would be greatly appreciated.
My question is, can I connect 480/277 wye to a 480 delta transformer and still power a subpanel that has a 240V 3 phase pump motor and (2) 120V circuits w/o any problems????
Any help would be greatly appreciated.