sandsnow
Senior Member
- Location
- Southern California
Backfeeding a delta / wye XFMR has come up numerous times. Most know not to bonded or otherwis connect anything to XO when used this way.
Yesterday I came across this old transformer. I'm not sure of the vintage. Maybe 1950's or earlier? It is installed in one of the hangars at the old El Toro MCAS. It was used as shore power to planes.
Note how XO is factory bonded to the case on the primary side. Seems to go against everything I've learned up to this point. I'm hoping someone has an explanation.
It also has a rating of 50 cycles which is unsual to me. A lot of equipment is dual rated 50/60, but I have never seen strainght 50 cycles.
Yesterday I came across this old transformer. I'm not sure of the vintage. Maybe 1950's or earlier? It is installed in one of the hangars at the old El Toro MCAS. It was used as shore power to planes.
Note how XO is factory bonded to the case on the primary side. Seems to go against everything I've learned up to this point. I'm hoping someone has an explanation.
It also has a rating of 50 cycles which is unsual to me. A lot of equipment is dual rated 50/60, but I have never seen strainght 50 cycles.