Thank you for that can you explain how to figure up voltage drop as you go farther and the load decreases. For example if I go the 1200 feet and then they add a 2 amp light load 600 feet farther down. THanks
One method is to find what's called the load center. Multiply each load by the distance from the source. Sum the preceding and divide by the total load.
For example, 1200ft ? 12A + 1800ft ? 2A = 18000ft-A... ? (12A + 2A) = 1286ft
Use 1286ft and 14A to calculate your voltage drop and determine wire size necessary for the entire 1800ft run.
Some methods use differing size wires between load points...
