jim3394

Member
Is there a proper method or a preferred method for entering a service panel with solid EGC. I am a industrial electrician with not much residential experience I am going to change out my service panel and want to make sure I do it properly.
 

480sparky

Senior Member
Location
Iowegia
Is it just me, or is that just a copper tubing clamp with a locknut on it??

Dang, first someone beat me to the pocket fisherman idea, then the "shamwow", and now this.

Steve

I'm sure there's some internal mechanism inside it to make a mechanical/electrical connection to the GEC. But their hype about being the only approved method is horse hockey, IMPO.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
An EGC should never enter the enclosure by itself. It must be run with the associated circuit conductors. I assume that the question is really asking about a GEC (grounding electrode conductor).
 

480sparky

Senior Member
Location
Iowegia
Ditto and the fact they try to lead people to believe that you need that product to comply with the NEC is enough to make me not to ever do business with them.

What I remember is some AHJ out east (New Jewsey?) has been convinced (or conned) into requiring them.
 