What is the formula and best way to figure voltage drop for a 20amp circuit 120v feeding driveway lights 1200 feet away. The wire will be in PVC conduit and the total amperage for the fixtures will be 12amps. Thanks
Thank you for that can you explain how to figure up voltage drop as you go farther and the load decreases. For example if I go the 1200 feet and then they add a 2 amp light load 600 feet farther down. THanks
One method is to find what's called the load center. Multiply each load by the distance from the source. Sum the preceding and divide by the total load.
Some methods use differing size wires between load points...