We got an mining facility at 4500m altitude asl. We got some panels 380V/219V, 50Hz fed from a 380V-380/219V, 75kVA, 3.1% aux transformer. The only protective device for the xfmr and panel is incoming breaker of xfmr which is 175amps fed from our MCC.
The distance from incoming breaker to xfmr is about 40ft while the panel and xfmr are next to each other. I referred to NEC 450 and 240.21 for xfmr protection and cable protection...I'm lil bit confused with various options on xfmr primary and secondary protection.
Could anyone assist me if I need to put a main CB in the panel or my incoming breaker should do? It's not about $, but looking at code requirement.
Thanks in advance
The distance from incoming breaker to xfmr is about 40ft while the panel and xfmr are next to each other. I referred to NEC 450 and 240.21 for xfmr protection and cable protection...I'm lil bit confused with various options on xfmr primary and secondary protection.
Could anyone assist me if I need to put a main CB in the panel or my incoming breaker should do? It's not about $, but looking at code requirement.
Thanks in advance