HELP - Per unit impedance for Short Circuit calculation
eestudent
In the general formula for per unit impedance
Zp.u(old) = (Powerbase(new)/Powerbase(old)) x (Zp.u(old)) x ([V(old) / V(new)]^2)
if I use the MVA(scc) of utility as powerbase
For Zp.u.(utility)= Power Base(new)/ Power Base (old)
where in :
voltage is said constant, why ?
there is no Zp.u(old), why?
For Zp.u.(transformer)= Power Base(new)/ Power Base (old) x Zp.u(old)
where in :
its Zp.u(new) = (Powerbase(new)/Powerbase(old)) x (Zp.u(old)) x ([V(old) / V(new)]^2) (1)
where in :
V(utility) usually is equal to V(base) so if you say:
Zp.u(old)=Powerbase(old)/V(base)^2 and
Zp.u(utility/new)=Powerbase(new)/V(utility)^2
since V(base)=V(utility) then,
Zp.u(utility)=Power Base(new)/ Power Base (old)
where in :
same as before usually V(transformer)=V(base) in both sides. If it is not, say you move one tap in the transformer in the secundary side, then you have to use the equation (1) of above
can't get it yet
can't get it yet
thanks for correcting Zpu(old) to Zpu(new)
Using the Utility's MVAscc as the commonbase you are right
V(utility) = V(base)
But if the transformer is connected in that Utility using the same
common base (Utility MVAscc) why the voltage of transformer
not been considered ?
Zp.u.new(transformer)= Power Base(new)/ Power Base (old) x Zp.u(old)
thank you !
If I understand your question, Mayimbe has answered that already:
In other words:
V(base)=V(utility)=V(transformer)