ARTICLE 310? CONDUCTORS FOR GENERAL WIRING
310.8 Locations.
...
(C) Wet Locations. Insulated conductors and cables used
in wet locations shall comply with one of the following:
(1) Be moisture-impervious metal-sheathed
(2) Be types MTW, RHW, RHW-2, TW, THW, THW-2,
THHW, THWN, THWN-2, XHHW, XHHW-2, ZW
(3) Be of a type listed for use in wet locations
(D) Locations Exposed to Direct Sunlight. Insulated conductors
or cables used where exposed to direct rays of the
sun shall comply with (D)(1) or (D)(2):
(1) Conductors and cables shall be listed, or listed and
marked, as being sunlight resistant
(2) Conductors and cables shall be covered with insulating
material, such as tape or sleeving, that is listed, or
listed and marked, as being sunlight resistant