A 4600 volt4/0 three conductor copper cable is in isolated conduit in air. What is the maximum allowable rating of a circuit breaker used to protect the ungrounded conductors?
The answer says 1200 Amperes
Ref: Table 310.75 & 240.101(A)
What is confusing me 240.101(A) says that the breaker cannot be six times the ampacity of the conductor.
Table 310.75
4/0 255A 90 c (Column)
285A 105 c (Column)
How do you get the 1200A?
Table 310.75
285A 105 c (Column)