Breaker Ratings
A-1Sparky
Vermont
Just wondering if each pole of a 3 pole 20 amp breaker is rated for 20 amps. Basically, can you have say, 17 amps on A phase, 18 amps on B phase, and 18 amps on C phase and not have the breaker trip on thermal overload? Or is it the combination of all 3 phases that's rated for 20 amps? :confused:
What's your take on it? Its 20A on each, or why else could you take three 20A SP CBs and tie them together and achieve the equivalent of a 20A 3P CB?
Here's a hint: multi-pole breakers are usually two or three single-pole breakers with common-trip mechanisms added and the bodies riveted together. You get more power from the same current by having more than one line conductor.