After using Art. 220 to compute the load for a small apartment, my calculation yields 63A.
Does the NEC permit the use of a 60A service(if so, what article) or is a 100A service required?
Thanks in advance
Thanks in advance
230.79(C) & (D) 100 amp for a one family dwelling, for all others 60 amp
If the calculation is 63 amps you need at least a 63 amp service.
If it where me I might check over my calculations and find a 3 amp mistake.
That is the disconnecting means only, not the service size.
Usually one in the same with breakers but use a fusible switch and anything goes.![]()
If the calculated load is 63 amps, why would anyone even think about trying to get away with a 60A service?
The 60A service is existing and the owner added a heat pump that is 2.5x larger than the space requires.
Are you trying to make a case for a smaller heat pump?