dpeter
Member
- Location
- Indianapolis, In.
- Occupation
- elevator mechanic / building maintenance
This is just what I need but so far none of the supply houses seem to be able to find it in any of their books. This is a 240v single phase with nuetral and ground recepticle. The reason it is needed is our church wants to do a fish fry fund raiser and the company that will be doing the cooking has 12KW 240v single phase fryers. HE SAYS all you need is a sixty amp breaker on a fifty amp range outlet that he will plug into or he can just hard wire onto the breakers and run out the panel and to his trailer.
Hard wiring to the panel is not going to happen and I cannot find in the code that says it's OK to overload a recepticle.
So I have two questions... Is the 14-60R recepticle available and second is there an exception for cooking equipment that would allow this load on a fifty amp recepticle. Oh and this a 208/120 panel and would be a 57.7amp draw.
Thanks for any help and direction.