stray voltage
j rae
I have a set of 150 watt H.P.S. street lights. One of my aluminum poles is reading 85 volts to ground. I have disconected the head and drove a ground rod still have the voltage. Any ideas ??????
How are you measuring this? and with what? I doubt you have, what you think you have. If it's TRULY voltage on the pole, driving a rod will not fix it. You need a low resistance path back to service. Is there an EGC?
I am useing a Fluke meter from pole to ground and I was shocked by the voltage.
That's probably a high impedence meter that is measuring the dfference in these two points,,,but,,If you were shocked, there's no denying that. You have a fault in the light or in the wiring. There is a problem with your EGC getting this fault back to the service. String a groung to service and measure with a wiggy from pole to the KNOWN GROUND.
... in more ways than one. ;)
Remember, voltage is a difference between points. The question is which one has the voltage above earth.
Either the EGC is energized, or there's a fault to what should be bonded, possibly inside the fixture itself.
Is the EGC connected to the pole when you take this reading?
Where are you getting your ground reference?
Are you able to cut only the light pole circuit off and then take the reading again? Just to be sure it's coming from the light circuit and not an outside source.