Conduit sizing

Status
Not open for further replies.

Bowen

Member
This may be a stupid question, but here it goes.

I have a 3c #6 W/Ground UF cable it measures aprox. 1-1/2" wide and maybe 3/8" thick, can I assume it would go in a 2" PVC conduit or can I somehow size the conduit mathematically?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You would size it as if it were round using it's widest dimension. Look at note #9 in Chapter 9 Tables.

Welcome to the forum. :)
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
This may be a stupid question, but here it goes.
Not a stupid question at all, but you might feel that way about the answer.

It may pay to terminate the UF and connect to individual conductors, depending on the situation, of course.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
Assuming your sleeving the UF for physical protection where it exits the ground, there are no sizing requirements. As long as you can get it to fit in the conduit, is all that matters.

Chapter 9 Tables, Notes to Tables (2)
 

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
...I have a 3c #6 W/Ground UF cable it measures aprox. 1-1/2" wide and maybe 3/8" thick, can I assume it would go in a 2" PVC conduit or can I somehow size the conduit mathematically?

Area = (R * R) * 3.14(Pi) Note 9 to Tables in Chapter 9, I come up with 2-1/2" Sch 40.
 