If you are in a live 480v MCC and you are rewiring a bucket what catagory would this be????
The incident energy inside of the bucket is the same as that of the busbars behind it, unless there is total isolation. I doubt that an existing MCC would have sufficient barriers to provide total isolation. There are stories of screws and even screwdrivers sliding through the space around the bucket and causing a fault.I meant that the mcc is on but the bucket is off and locked out. We all know that there is still energized parts in the bucket at the top of the breaker.
The incident energy inside of the bucket is the same as that of the busbars behind it, unless there is total isolation. I doubt that an existing MCC would have sufficient barriers to provide total isolation. There are stories of screws and even screwdrivers sliding through the space around the bucket and causing a fault.
The bucket is deenegized and locked out. But we know there is still energized parts in the bucket.
I personally can do on the spot HRC analysis, and your MCC is a class 4.
You are amazing, please show your work. How did you come up with 4?
What if this is in a paper mill where the MCC's are commonly fed by switchgear with no main breakers and feeder breakers without INST trips, giving the MCC's long clearing times with the already high fault currents?
I knew this comment would bend you out of shape.![]()
Removing a bucket from an energized MCC can be a high risk operation requiring significant safety evaluation. Working on a deengergized bucket is a better solution. Older MCC's have the connection to the bus somewhat exposed but recently I have been purchasing MCCs that have a plastic barrier that isolates the high volage side of the breaker from the rest of the bucket. You can also purchase retrofit kits to do the same thing. In this case, if the breaker has been opened and verified, the high voltage is no longer exposed nor are you interacting with it since it is protected from accidental contact. If you make provisions to prevent parts from falling into the bucket below, then you should be able to work on the low voltage side of the deenergized bucket wearing minimal PPE.
Comments?
Thats why remote extraction is becoming so popular.