testing lights with emergency battery ballast
anbm
TX
Designer
One of the folks asked me, if he has around 150 fluorescent lights (with emergency battery ballast and test switch) installed on high ceiling around
22 feet. Contractor do not want to climb up there and test light by light to make sure emergency bat. ballast works. It will takes a lot of their time. This test is required monthly.
My suggestion is they go to the panel and flip the CB which controls circuit has those bat. ballasts light add see if the bat. ballast kick on when loosing power. Is there any other simple solution for this? I heard something like remote test switch but that will add cost to project. Thanks!
Low tech solutions are still the best IMO, shutting off the breaker(s) is a good way to test them.
Roger
If only a brief test test is required then this may be done whenever convienient, by turning off the breaker(s).
If however a full discharge test is required, then IMHO it should be done outside of working hours, to ensure that the batteries are recharged before the building is next occupied.
I'm just shocked someone is actually going to test these things. On a monthly basis no less.
I know its code, but after the initial inspection, I think this stuff is normally just forgotten.
Steve
Per NFPA Life Safety Code 101 section 7.9.3.1.1 they are supposed to be tested once a month to make sure they work and annually for 1 1/2 hours.
IMO turning off the breaker is the best way to do this.
Now all yo have to do is figure out which breakers are used for the lighting :)