Currently working at a facility that has 2 Big Generators. Each Generator has a EM Distribution Panel a ways away from them inside the Facility on the top floor. Thier both 480/277 going to 2 identical Panel boards Main Breaker'd at 800 amps each. Each panel subfeeds 2 or 3 small ATS's. The two EM panels are mounted right beside each other. There is a extra 800 amp breaker in each panel making a jumper between the two. There's locks on the jumper breakers and are always locked off. Way it was designed so im told is if one GenSet Fails, its feed can be shut off at the main breaker in the panel. and the 2 aux breakers opened up. One GenSet take up the slack where the other failed. My concern or question is not with this setup. I actually like the idea. It's with the neutral conductors im questioned. There is 2 jumper wires going from panel to panel. Which is a good thing, when one GenSet is Locked out. But if things are working 100%, everythings normal. Isn't both panels neutral bonded together ? The facility's been up for 5+ years and they say there's no problems with it that they've noticed. Im just wondering if both GenSet's are running and both supplying power to thier individual panels like thier suspost to be doing. What are those 2 600MCM's going from panel to panel neutral bus doing to it. Shouldn't i need some kind of Switch to isolate the 2 neutral bus's? Im by far a engineer or know about harmonics and waveforms. Just looking for some advice and education. Thanks as always.... Hector/.