334.15 c
A/A Fuel GTX
WI & AZ
I thought there was an exception to 334.15 C that would allow fastening NM-B smaller than #6 0r #8's directly to the lower edges of the floor joists without having to bore holes if there was a dropped ceiling being utilized. Can someone enlighten me?
Here, if a drop ceiling is utilized it is not longer an "unfinished basement", so 334.15(C) doesn't apply. The downside is 210.52 does.
334.15 is for exposed work. If above a ceiling, it won't be exposed.
Volta, what about:
Exposed (as applied to wiring methods). On or attached to the surface or behind panels designed to allow access.
(food for thought) :)
Volta, what about:
334.15 (c) does not use the word exposed, it only says unfinished basements, if the basement meets requirements of 210.52 for being finished, then 334.15 (c) does not apply, I WILL NOT agree that a ceiling ALONE makes this a finished basement, It takes required outlets and ceiling to make it finished, IMO
I will agree. I "ceiling=unfinished" has been more an accepted practice here than actual NEC. From your comment, I would think we are both in agreement it must meet 334.15(C) or 210.52, correct ?
Volta, what about:
Good point. I'll be thinking about that one. Hard to say that a grid ceiling doesn't contain panels designed to allow access! I wonder why the definition is written that way . . . :confused:
A "Catch 22" , I think. Were it not worded that way you would not be allowed to place J boxes there.
Probably so other requirments in the Code,to not conceal componets of various wiring methods does not restrict such installations in suspended ceilings.
The determination of whether a basement is finished or not is not part of the NEC, it is a building code. My experience of how building departments deteremine what is and is not a finished basement is not the same from jurisdiction to jurisdiction. I believe it is up to the inspector and the installer to be aware of what each municipality is using to determine a finish or unfinished basement