Voltage Drop

Status
Not open for further replies.

rheydel1

Member
Voltage Drop

I meant the maximum allowable voltage drop allowed on a motor circuit and where do I find that in the N.E.C.
 

iMuse97

Senior Member
Location
Chicagoland
See 210.19(A) FPN No. 4 (where FPN stands for fine print note). As many on this forum will tell you, the fine print is not enforceable code, but with motor applications you don't need excessive voltage drop, but then you know that being in a plant.:grin:
 

drbond24

Senior Member
The NEC only provides recommendations for maximum voltage drop, not requirements. If you are wanting to know the lowest voltage at which the motor will still operate properly, I'd ask the manufacturer.
 

mivey

Senior Member
What is the maximum voltage allowed on a motor circuit and where do I find this in the N.E.C.
From ANSI C84.1:

Normal operation: 108 to 125 on a 120 volt basis. Should operate satisfactorly.

Infrequent operation: 104 to 127 on a 120 volt basis. Might operate at acceptable performance levels. Protective equipment might take motor off line.

Abnormal levels:<104 or >127. Protective equipment will probably take the motor off line.
 

skeshesh

Senior Member
Location
Los Angeles, Ca
VD

VD

The nec doesnt have requirements only recommendations as stated. For motor application I'd agree with drbond24 - you should get your hands on some data sheet or spec from the mfg. to see what the operating voltage is, then size to keep the drop in range of operating voltage.
 