Ditto!
Typically, you'd just drill and tap a two or three holes on the panel's rear surface, say 8-32, and mount the strip with two or three matching screws.
I always remove and save unused grounding strips from panels when I install them. You never know when you'll need to add an extra bus strip.
I disagree with this procedure.
1. Manufacturers list products and have instructions for locations for the installations of terminal strips in their enclosures.
2. drilling and tapping holes in the enclosure may not provide one with the 2-threads minimum necessary for termination.
Fault current is going to be flowing across the screw termination into the the metallic enclosure, it is essential that the termination does not increase the impedance of the fault current path. If one is going to install a terminal bar to the enclosure, I suggest the use of a bolt and nut, with the appropriate washers.