Hey guys and gals!
New to the site and wanted to post a question for you all.
According to the 02' code book (I know, I need to get the 05' or 08' but I am sure it is still the same verbage), Article 250.52 (B)(1) Metal underground gas piping systems are not permitted as grounding electrodes.
Also in Article 250.104(B) Gas piping is required to be ("shall be") bonded to the service equiptment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used.
In a way these two seem to contain a contradiction but I may need some clarification on how to interpret what is being stated here.
My question is simply if one is allowed to bond the gas piping system to one of the grounding electrodes, doesn't that - at least mechanically make it part of the grounding electrode system? I assume that the code means to eliminate the gas piping system as being the only grounding electrode or as the supplimental. For instance, having the underground water and gas piping systems serve as the GES.
Does anyone know the reasons why the gas piping system is not permitted to be a GE?
Thanks
Thanks