I recently installed a temporary 3-phase 120/208 service to a retail space that was newly renovated (and waiting on the POCO to install a meter).  I ran a short (20') 3-phase SER cable from an adjacent store and an existing 200 amp main lug panel.  I used a 3-pole 90 amp Siemens breaker in the 200 amp panel and landed the other end of the SER on the main lugs of the new panel.  
Now, I accidentally shorted the EGC to a phase conductor while changing out an exit light in the new section. The 20 amp circuit for the exit lights in the new panel didn't blow but the 3-pole 90 in the 200 amp panel did. Does anyone have an idea why the 3-pole 90 blew before the s/p 20 amp breaker did ?
Thanks in advance.
Phil
	
		
			
		
		
	
				
			Now, I accidentally shorted the EGC to a phase conductor while changing out an exit light in the new section. The 20 amp circuit for the exit lights in the new panel didn't blow but the 3-pole 90 in the 200 amp panel did. Does anyone have an idea why the 3-pole 90 blew before the s/p 20 amp breaker did ?