corner grounded delta 3 phase 240 volt

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
Lets make this simple . Can you land the grounded service conductor of a three phase corner grounded delta on a over current device.(breaker or fuse)
 
corner grounder delta

corner grounder delta

No! It's a different question.
 
Yes you can.


02ajohnston_fig5_986883029.jpg

this illustration is from an IAEI piece
 
Lets make this simple . Can you land the grounded service conductor of a three phase corner grounded delta on a over current device.(breaker or fuse)
Breaker yes, fuse no, unless the fuse is used to provide motor overload protection
 