grounds entering panel boards

Status
Not open for further replies.

101010

Senior Member
I am interested to see when you guys enter a panelboard with your ground wires ( bare or insulated) do you use kenny clamps ,romex connectors or nothing?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If you're talking about residential panels, I use the 3/8" KOs and no connectors.

In a larger panel, with a larger GEC, I might use a 2-screw cable clamp.
 

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
If you're talking about residential panels, I use the small, what looks like a 1/4" KO that is in a 1/2" and no connectors. Most all panels I install are no larger that 200 amp.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
For commercial panels our GEC's are in conduit. For residential we would just use the small KO in the panel. For years we used a Romex connector for the GEC but after reading here that they're technically not listed for single conductors we've been using the small KO's. Even with the Romex connectors we were never issued a violation in 25 + years.
 