I have a situation where I need to calculate the adjustments for both temp. and for CCCs.
Using #12 Cu. THHN/THWN 20 amp loads with 6 CCC 4? above roof in EMT.
Calculations:
Table 310.15(B)(2)(c) 4" = 30deg adder
Using a design temp. of 94deg
94 + 30 = 124deg.
Table 310.16
#12 @ 90deg = 30 amp
Correction factor for above calculation @ 90deg is .76
Load = 20 amp / .76 = 26.31 or 26 amp
So: 26 amp * .80, for 6 ccc, = 21 amps
I can still use #12 with a 20 amp load after all corrections?