I have a question for calculation and feeder ampacity for each segment of the circuit. I have calculated 120 amps for (4) 50 amp pedestals. With 75% demand factor, the feeder should not have trouble with heat and a/c loads?
Also with 125 amp breaker, I thought the wire should not be less than AWG #1 at any segment of the circuit, even if the last pedestal sees only 50 amps.
Is this correct?
Also with 125 amp breaker, I thought the wire should not be less than AWG #1 at any segment of the circuit, even if the last pedestal sees only 50 amps.
Is this correct?