34.5KV Line loss
cinch08
New member
What is the easiest way to figure your line loss on a 34.5kv overhead powerline. I had someone ask me this question, they are trying to figure out what size of wire to use on a wind turbine project.
Do you want line loss or voltage drop?
For power systems:
kWh loss/yr/mile=
(peak kW)^2 * (Resistance per phase per mile) * (Loss Factor) * 8760
divided by
kV^2 * (power factor)^2 * (Number of phases) * 1000
and where (Loss Factor) = 0.84 * (Load Factor) + 0.16 * (Load Factor)
This will be the way I'll do it:
1) choose a size of wire
2) Get the R (ohms/miles) value
3) Get the current that will flow on that line
4) then:
Ploss=I^2*R