I thought NM was to be rated per the 60-deg column.
14 = 20a
12 = 25a
I would say this portion of the NEC (334.80) would affect the ampacity of a conductor for 240.4(G).
Although 240.4(D) restricts standard fusing size, such as 15A - for 14 AWG, 240.4(G) would permit in some installations to increase the size of the OCPD, which would be greater than 15A- for 14 AWG.
But, 334.80 will restrict the use of NM to no greater rating than the 60C column, regardless of 240.4(G).