Any code violations here?

Status
Not open for further replies.

nhfire77

Senior Member
Location
NH
Well it depends. Are any of those tied to a fire alarm system? What are the outputs to? Is it class 2 or 3, then again that may not matter.

wait a sec, is all the secured to a DUCT? that might be an issue.
 

stevenj76

Senior Member
Couldn't you have just bought a 5-channel power supply???!!??
Then nippled on a recep in a handy box? Is that wall-wart going back to a modem or repeater or something?
 

stevenj76

Senior Member
Yeah, they are Class 2, probably 48VA each.
The controls folks usually supply that stuff. Next time tell them you want it in a can.
 

cpal

Senior Member
Location
MA
Is that 3/8" FMC coming in from the upper left feeding this conglomeration of power supply's?

3/8" FMC can not feed an outlet box. 348.20(A)(1)-(5)

Possibly 300.22(B)

348.20 Size.
(A) Minimum. FMC less than metric designator 16 (trade size 1/2) shall not be used unless permitted in 348.20(A)(1) through (A)(5) for metric designator 12 (trade size 3/8).

(2) In lengths not in excess of 1.8 m (6 ft) for any of the following uses:
a. For utilization equipment

I don't see wher this section restricts a receptical suppying plug in utilization eq.
 

stevenj76

Senior Member
I don't see wher this section restricts a receptical suppying plug in utilization eq.

I would not install a ball of crap like that because of Art. 110, neat and workmanlike manner.

Who installed that? A pipefitter who drank two pots of coffee?
 

Stallzer

Member
Location
MN
I do believe that the wall wart plugged into the receptacle is a code violation if indeed that is a plenum rated space.....unless of course this person is using a plenum rated wall wart, which I doubt.
 

stevenj76

Senior Member
That's right about the wallwart, no wallwarts in plenums or above the grid.

Looking at the install, I would double check the wiring to make sure it was all wht/blk and blu/brn. You don't want 120 coming in on the 24v winding, it starts making funny noises.
 

TLBryant

Member
Location
West Virginia
I would be concerned about conductor fill in the metal boxes. I would not install a receptacle in a plenum unless it is inside another enclosure - violation of NEC 300.22 (C) (2). Maybe I'm too picky, but what about NEC 110.12 - the most violated code in the NEC?
 