Recently I was contacted by a local university to 'put wire nuts on some recently replaced wire'. Upon further inquiry, I was told that the university was doing an outside experiment measuring the effects of global warming and had some outside heaters being used to simulate the suns heat, and one of the circuits powering a particular set of heaters had a fire and 'they' replaced the wire, but needed wire nuts put on the splices. So, I said I would 'assess' the situation. This is what I found: 8 heaters ( each one about the size of a shoe box) radiant type...4 each at one location, 4 at the next location, about 10 feet apart. 1000 watts each, fed by 277 volts. The fire ocurred in the junction box of the first location. Circuit consists of #10 thhn, protected by a 35 (yes 35) amp breaker. Now, maybe I am wrong, but as I see it, 1000 watts x 8 = 8000 watts/277 volts= 28.88 amperes load. Given they are heaters, operating for more than 3 hours, multiply 28.88 x 1.25 % = 36.10 amperes. That should mean that the circuit should have #8 thhn as a conductor, not #10. The breaker should be 40 amperes. Am I right?