Friday's STV.... a --real-- shocker!

Status
Not open for further replies.

480sparky

Senior Member
Location
Iowegia
Yet another panel swap today.

First thing I see:

DSC_5566.jpg


DSC_5567.jpg



OK, easy fix.... I can replace it when I'm done.

So I pull the meter and get to work.

I pull the cover off and see this:

DSC_5568.jpg




I start taking wires off breakers and WHAM! I get hammered. Service conductors are removed from main breaker, and the meter has been pulled.

DSC_5569.jpg


The large wires that look like copper are aluminum with brown de-ox on them.

So I tape it up, and keep going. I get to the neutrals and WHAM! I get hammered AGAIN!

DSC_5571.jpg


Yippee!
 

480sparky

Senior Member
Location
Iowegia
STV, Part Deux

STV, Part Deux

So my buddy is running some 10/3 for a new dryer, and he spots these little gems above the grid:

DSC_5579.jpg


DSC_5577.jpg


DSC_5578.jpg


Sigh.........
 

480sparky

Senior Member
Location
Iowegia
STV, Part Tre.

STV, Part Tre.

So we also need to locate a short in a circuit.

Trace it to some conduit outside. NM inside.

DSC_5583.jpg


DSC_5582.jpg


DSC_5581.jpg


DSC_5580.jpg




Thank God It's Friday.:cool:
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Didn't I just read a statement from you; "non-contact voltage testers are useless"? Whats that in your hand?
 

480sparky

Senior Member
Location
Iowegia
Didn't I just read a statement from you; "non-contact voltage testers are useless"? Whats that in your hand?


Yea, well, trust me.... it was live. Actually, they were. I just had the camera and the NCT handy. I didn't want to take the time to go get my meter out of the van.
 
Last edited:

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
I didn't want to take the time to go get my meter out of the van.

Well, I wouldn't start that type of work without a tester within arms reach. Glad your OK pal. Is this where we start guessing why you were energized with the meter pulled?:grin:
 

480sparky

Senior Member
Location
Iowegia
Well, I wouldn't start that type of work without a tester within arms reach. Glad your OK pal. Is this where we start guessing why you were energized with the meter pulled?:grin:

Well, when you pull the meter and go back in to find all the lights, fridge, stove, etc. not working, you kinda get the idea the panel is dead.

So yea, any ideas why I had two hot wires with the meter pulled?
 

480sparky

Senior Member
Location
Iowegia
Doesnt make sence... does the meter have a bypass? Do they have solar? Do they have a generator? Do they have a UPS hooked up the wrong way? Were they stealing power from another source?

~Matt


Well, the best hint I can give you is this is in a duplex......... :roll:
 

480sparky

Senior Member
Location
Iowegia
I think we have a winner....:)

The only thing I can think of, since there's no house panel, is that a circuit was fed from both panels to power the exterior lights.

But the noodle must be in this panel only, or else it wouldn't show hot or spark when I terminated it.
 

480sparky

Senior Member
Location
Iowegia
So, What are you goign to do with that circuit? Hook it back up? Leave it? Fix it?

~Matt

I landed the neutral on the assumption it's for something as it is drawing power.. it arced when I did so. I left the hot undone.

I need to contact the landlord to discuss the other issues we've found.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
I've got a good one on Tuesday to repair. It's a service built on a stanchion for a farm, I'll have to remember to take before/after pics.:)
 