Is it code compliant to use a bonding jumper between a ground rod and the metal frame of a building? Does that make the building frame bonded?
I thought you had to land the jumper on the ground bus, or water pipe, but I could be wrong.
Thanks for any help, and code ref.
 
You can bond all the parts of the grounding electrode system together with bonding jumpers.

1113918256_2.jpg
 
Just keep in mind you will still need to have the proper sized GEC's and bonding jumpers when using this method. For example, if a #3/0 is required going to building steel you can not hit the rod with a #6 GEC and then go from the rod to the steel with a #3/0 bonding jumper.
 