Are welders considered cont. use ? I have five to wire the name plate max amps is 41 . I am pulling #8 on 50 amp breakers , and installing 50 amp 480 3/p 4 wire plug and recp. Is this correct?
Are welders considered cont. use ? I have five to wire the name plate max amps is 41 . I am pulling #8 on 50 amp breakers , and installing 50 amp 480 3/p 4 wire plug and recp. Is this correct?
This is in a shop that builds trucks . I have done a lot of work in this shop and never seen any welder used for three hours none stop. On but not in use.
Are welders considered cont. use ? I have five to wire the name plate max amps is 41 . I am pulling #8 on 50 amp breakers , and installing 50 amp 480 3/p 4 wire plug and recp. Is this correct?
Papa, article 630.12(A)and(B) allow up to 200% of name plate. What is the duty cycle listed on the name plate. 41 amps x duty cycle x 200% = minimum conductor size, 41 amps x 200% = OCPD (next standard higher ok) but not more than 200% times conductor.
Rick
And actually if you think about it:
according to definition, there is no "continuous load" stick welder in this world. I've never seen a welding rod that last for 3 hrs.