Looking for a little help on this one , I've been asked to just supply power for an air compressor in a plant. so far the only information is the FLC is the standard FLC of 156 amps . I know that isnt much to work with, the feed is about 40 feet, Its coming from a Square D I-line panel 480v . Im not sure what type of starting device its coming with either .
430.22 125% x 156 = 195 amps
310.16 75c = 3/0
I guess in asking about the i-line breaker , with a 200 amp breaker will it handle the inrush current, I know im missing a lot of information but if i could get some input. thanks !
430.22 125% x 156 = 195 amps
310.16 75c = 3/0
I guess in asking about the i-line breaker , with a 200 amp breaker will it handle the inrush current, I know im missing a lot of information but if i could get some input. thanks !